GFCI Outlet - I'm going crazy!
Posted: Mon Oct 21, 2019 4:11 pm
I have replaced about a hundred GFCI outlets over the years and I never had a problem, and now I am totally stumped.
I bought three new ones, two different types. First one was to replace one in a bath that would not trip/reset anymore. I move the wires from the old one to the new one one wire at time so it would be hard for even me to screw up. I am very sure I did not mix up load side verses line side.
After I was done, I turn back on the power. I test the outlet by tripping and resetting the outlet. So far so good. What ever I plug into the GFCI outlet itself works properly. If I test it, the power goes out to whatever is plugged into the outlet when it trips. And when I reset whatever I have plugged into the outlet itself goes back on. So that is ok.
Problem is the down stream outlets I have hooked up to the "load" screws. They never get any power. I put a VOM on the load screw never show power. I see power on the line side. VOM sees power to the outlet prongs themselves when it is not tripped.
Outlet also has a self test and the light goes green when the power is first turned on, and yellow when tripped.
So I figure I got a defective new GFCI. So I pull out another one - the other manufacturer, and it does the same exact thing! No power ever to the "load" screws.
I install the third and same thing!
If I put a wire nut and tie the load wire to the line wire, I get power to the down stream outlets, but of course they are no longer GFCI protected!
Any ideas what is going on before I have to cave and call an electrician? I doubt I could get 3 defective ones in a row.
I bought three new ones, two different types. First one was to replace one in a bath that would not trip/reset anymore. I move the wires from the old one to the new one one wire at time so it would be hard for even me to screw up. I am very sure I did not mix up load side verses line side.
After I was done, I turn back on the power. I test the outlet by tripping and resetting the outlet. So far so good. What ever I plug into the GFCI outlet itself works properly. If I test it, the power goes out to whatever is plugged into the outlet when it trips. And when I reset whatever I have plugged into the outlet itself goes back on. So that is ok.
Problem is the down stream outlets I have hooked up to the "load" screws. They never get any power. I put a VOM on the load screw never show power. I see power on the line side. VOM sees power to the outlet prongs themselves when it is not tripped.
Outlet also has a self test and the light goes green when the power is first turned on, and yellow when tripped.
So I figure I got a defective new GFCI. So I pull out another one - the other manufacturer, and it does the same exact thing! No power ever to the "load" screws.
I install the third and same thing!
If I put a wire nut and tie the load wire to the line wire, I get power to the down stream outlets, but of course they are no longer GFCI protected!
Any ideas what is going on before I have to cave and call an electrician? I doubt I could get 3 defective ones in a row.